I would appreciate any information on [Interdit] following:-
EDF are going to connect 9KW power over 75metres length *9*9*9* domestic supply.
If I need 2 core cable of 35mm2 (do I?) where can I get this?
If I get [Interdit] cable, it is going to be very thick, [Interdit] can I [:(] connect it to at both ends, prior to EDF connecting it permanently?
Thanks *9*9*9* prompt replies.
New Supply electric cable
- RFco
- Modérateur & Admin

- Messages : 7312
- Enregistré le : sam. 22 mars 2008 19:13
- Localisation : Normandie
- Contact :
Re: New Supply electric cable
Hello,
sorry, but I only speak french.
*9*9*9* 75m and 9kW : 50mm² is [Interdit] lower limit,
@+
sorry, but I only speak french.
*9*9*9* 75m and 9kW : 50mm² is [Interdit] lower limit,
@+