I would appreciate any information on [Interdit] following:-
EDF are going to connect 9KW power over 75metres length *9*9*9* domestic supply.
If I need 2 core cable of 35mm2 (do I?) where can I get this?
If I get [Interdit] cable, it is going to be very thick, [Interdit] can I [:(] connect it to at both ends, prior to EDF connecting it permanently?
Thanks *9*9*9* prompt replies.
New Supply electric cable
- RFco
- Modérateur & Admin

- Messages : 7312
- Enregistré le : sam. 22 mars 2008 19:13
- Localisation : Normandie
- Contact :
Re: New Supply electric cable
Hello,
sorry, but I only speak french.
*9*9*9* 75m and 9kW : 50mm² is [Interdit] lower limit,
@+
sorry, but I only speak french.
*9*9*9* 75m and 9kW : 50mm² is [Interdit] lower limit,
@+
Ce qui se conçoit bien s'énonce clairement, alors, n'hésitez pas sur les détails...
Re: New Supply electric cable
Bonjour,
Pour ne pas déroger à la règle et bien que l'intention de lostinfrance ne soit pas mauvaise:
lostinfrance, thanks to speak french in this forum.
Cordialement / Cordially
Max
Pour ne pas déroger à la règle et bien que l'intention de lostinfrance ne soit pas mauvaise:
Précisons que cette règle est là pour que tout le monde puisse comprendre les divers sujets.Charte du forum a écrit : - Tous les messages doivent être en Français, l’utilisation de l’écriture SMS est à éviter.
lostinfrance, thanks to speak french in this forum.
Cordialement / Cordially
Max
Qui est en ligne
Utilisateurs parcourant ce forum : Majestic-12 [Bot] et 8 invités
